potterton profile 100e
not fireing air pressure switch and fan are fine
just .35 mbr at pressure switch.
no kinks in pipe work and flue is not blocked
 
Sponsored Links
121164 said:
not fireing air pressure switch and fan are fine


How do you know they're fine?

Does it spark?
Does the pilot light?

I guess your 43 in November
 
thanks for the reply
the air pressure switch opperates when you gently blow down red pipe on flue elbow and the boiler fires
with the casing on i am only getting .35 mbr on the pressure switch
on the same boiler next to it im getting 1.21 mbr
have checked for blckages twisted hoses and blocked flue all seem fine?

thanks baxipot
 
Sponsored Links
121164 said:
thanks for the reply
the air pressure switch opperates when you gently blow down red pipe on flue elbow and the boiler fires
with the casing on i am only getting .35 mbr on the pressure switch
on the same boiler next to it im getting 1.21 mbr
have checked for blckages twisted hoses and blocked flue all seem fine?

thanks baxipot

fan blocked or running slow, try swapping the fans over from the boiler next to it.
 
thanks chaps but flue is fine.
there seems to be no air loss around the casing seals ect

fans have been swapped and still get the same pressure differences?

have put airline down heat exchanger and is working ok
thanks for all your comments
 