DIYnot
Local | Network
   DIYnot > Forums
Local | Network
CHANGING A RAVENHEAT CSI 85 DIVERTER VALVE?
Goto page 1, 2  Next
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating
Author Message
Hottub
from United Kingdom
PostPosted: Tue Feb 20, 2007 11:45 am Reply with quote
Has anyone changed or know if its an easyish job to change a diverter valve on a condesing boiler?
Back to top
 Alert Moderators
Agile
from United Kingdom
Thanked: 2570 times
PostPosted: Wed Feb 21, 2007 1:22 am Reply with quote
The fact a boiler is condensing makes little difference to the work involved in changing a diverter valve.
I would be surprised if the diverter valve really needs to be changed! Why do you think it needs to be replaced?
Tony
Back to top
 Alert Moderators
ChrisR
from United Kingdom
Thanked: 945 times
PostPosted: Wed Feb 21, 2007 2:15 am Reply with quote
Looks easy enough - but then it is a Ravenheat...
Back to top
 Alert Moderators
HarrogateGas
from United Kingdom
Thanked: 8 times
PostPosted: Wed Feb 21, 2007 7:46 am Reply with quote
its not too badder job, bar one connection.
Back to top
 Alert Moderators
Hottub
from United Kingdom
PostPosted: Wed Feb 21, 2007 10:25 am Reply with quote
Tony
Thanks everyone for the info, Tony I am guessing its the diverter valve because the central heating works fine, its just the hot water to the taps that plays up, I have to keep resetting the boiler then the hot water works again for a while until I have to reset again! Boiler has just been service by a corgi reg plumber and said all was well! However fault is now getting worse. Thanks Wayne
Back to top
 Alert Moderators
ChrisR
from United Kingdom
Thanked: 945 times
PostPosted: Wed Feb 21, 2007 10:49 am Reply with quote
Check the microswitches on the end of the DV
Back to top
 Alert Moderators
Hottub
from United Kingdom
PostPosted: Wed Feb 21, 2007 10:54 am Reply with quote
Not sure how I would go about that?
Back to top
 Alert Moderators
Agile
from United Kingdom
Thanked: 2570 times
PostPosted: Wed Feb 21, 2007 11:18 am Reply with quote
Tony
If the boiler fires up when a tap is turned on then clearly the diverter is working.
This "resetting" sounds as if it may be an overheating or combustion related failure which is nothing to do with the diverter valve!
Tony
Back to top
 Alert Moderators
Hottub
from United Kingdom
PostPosted: Wed Feb 21, 2007 11:31 am Reply with quote
Tony
If the boiler is tuned to water only it never runs hot water to the tape it only seems to work when heating and water are both on?
Many thanks Wayne
Back to top
 Alert Moderators
ChrisR
from United Kingdom
Thanked: 945 times
PostPosted: Wed Feb 21, 2007 11:49 am Reply with quote
If the switch isn't getting operated you'd get no hot water unless you have the CH on, which is what you've got.
If the DV/switch was sticking in HW position, I wouldn't be surprised if the boiler overheated.
So intermittent "mucking about" could all come down to the DV.
When the hw is turned on the pin should come right out smartly and press the switch fully, and go back equally smartly when the tap goes off.
The switch contacts should make clean open/closed circuits.
Quick to check if you know how - otherwise you need an engineer.
Back to top
 Alert Moderators
Hottub
from United Kingdom
PostPosted: Wed Feb 21, 2007 12:05 pm Reply with quote
[quote="ChrisR"]Check the microswitches on the end of the DV
O.k. Many many thanks for your help/advise ill try and check the pin operation, might try and change the diverter valve tonight if I get stuck, ill have to call the gorgi guy back!
Many thanks everyone!
Back to top
 Alert Moderators
Hottub
from United Kingdom
PostPosted: Thu Feb 22, 2007 2:54 pm Reply with quote
I was going to change the diverter valve last night and turned off all the valves etc, I then unscrewed the bleed nut and very high pressured water shoot out so I quickly put the bleed nut back on!
Does anybody know if the water should come out this pressurised or maybe there’s something I haven’t turned off?
Thanks Wayne
Back to top
 Alert Moderators
ollski
from United Kingdom
Thanked: 51 times
PostPosted: Thu Feb 22, 2007 5:27 pm Reply with quote
The water will still be sat in the boiler and in the pipes at the system pressure. You need to isolate it as you have done and then drain the boiler itself making sure the aav is open also open all your hot taps so the water can run out when you undo the connections and let the air in. That will minimise the water you will come across but still make sure all the electrics are well covered.
Back to top
 Alert Moderators
Paul Barker
from United Kingdom
Thanked: 468 times
PostPosted: Thu Feb 22, 2007 6:17 pm Reply with quote
But has been said you might not need a new diverter valve. You might need a thermister or a microswitch, or at worst a diaphragm. If you need to ask these questions but without the ability to describe the situation more fully, you are demonstrating that your conclusion isn't intelligently arrived at. It would be down to luck now as to whether you have plumbed for the right part. It is one valid way to fix a boiler, to just throw parts at it. Works for the spotty youths working for a once respected national gas supplier.
Back to top
 Alert Moderators
Hottub
from United Kingdom
PostPosted: Fri Feb 23, 2007 10:23 am Reply with quote
O.k. thanks, I’ve now changed the diverter valve and heating and hot water working fine, did take the old diverter valve apart and all looked o.k. in there, the diaphragm wasn’t split but obviously something was wrong!
Once again many thanks for all your knowledge/help!
Wayne
Back to top
 Alert Moderators
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Goto page 1, 2  Next
Page 1 of 2
Jump to:
Changing diverter valve/O rings: help needed 5 760 Tue Jan 03, 2006 2:56 pm
Ravenheat 3 way diverter valve replacement costs 2 340 Sat Mar 27, 2010 9:47 am
ravenheat diverter valve 2 200 Sat Oct 10, 2009 2:50 pm
Ravenheat RSF 820/20 boiler - diverter valve 4 760 Sat Apr 10, 2010 9:17 pm
Ravenheat 820 Diverter Valve Problem 6 840 Sat Sep 30, 2006 5:31 pm