Posted: Tue Feb 27, 2007 4:05 pm Post Subject: Panel Heater |
 |
|
I needed to extend the flex of my 800w panel heater as it was situated a some distance from a plug. The flex that ran from the heater was 0.75mm so I bought some more of this and wired it up using a 3 terminal connector. My concern is that the guide says that the 0.75mm flex is for 6 amps where as the heater is only 3 amps. Would this cause a problem? |
|
davy_owen_88

Joined: 17 Nov 2006 Posts: 1680 Location: West Glamorgan, United Kingdom Thanked: 0 times
|
Posted: Tue Feb 27, 2007 4:22 pm Post Subject: |
 |
|
6A > 3A so no, there won't be a problem. It's fine to use cable with a higher rating than the appliance it is connected to.
Davy |
|