PRISMA 24SE TURNING OFF ON DEMAND FOR HEAT

This topic originated from the How to page called Problems associated with noises from the central heating system
Click here to return to the page called Problems associated with noises from the central heating system.

 
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating
  View previous topic :: View next topic  
Author Message
seegee

from United Kingdom

Joined: 27 Jun 2007
Posts: 2
Location: United Kingdom
Thanked: 0 times

PostPosted: Wed Jun 27, 2007 1:02 pm    Post Subject:
PRISMA 24SE TURNING OFF ON DEMAND FOR HEAT
Reply with quote Thanks

My PRISMA 24SE TYPE C Will start up ok when water is turned on ,then the heat will come through , after a few seconds say 15 , the flame goes off the heat will still rise and then drop back - the flame then relights to follow this cycle again

THE PROBLEM IS THE SHOWER RUNS COLD THEN HOT AND NOT AT AN EVEN OUTPUT.

when the central heating is put on the flame stops on till the heat switches the thermostat then it cuts in and out in the same fashion . the switch on the diverter works so does the tell tail to the switch the relay for the sink hot water comes on
but the one that controls the gas sol. switches off (I assume this is because either the water is getting too hot or something sensing the water is out of range?) there are two sensors the first is under the pump ,the other is by the diverter valve these are working. the end cap on the pump once undone shows the pump revolving and not under load . I have checked the air flow is clear of any blockage.
Back to top
 Alert Moderators

If you don't want to see this advert, click here to login or if you are new click here to join free.
rob884

from United Kingdom

Joined: 14 Aug 2006
Posts: 2290
Location: London,
United Kingdom
Thanked: 2 times

PostPosted: Wed Jun 27, 2007 5:14 pm    Post Subject:
Reply with quote Thanks

Plate HE is probably blocked. Best to replace but is possible to clean out although its much messier!
Back to top
 Alert Moderators
ChrisR

from United Kingdom

Joined: 24 Jul 2003
Posts: 18661
Location: London,
United Kingdom
Thanked: 62 times

PostPosted: Wed Jun 27, 2007 8:27 pm    Post Subject:
Reply with quote Thanks

WOUldn't affect the CH though rob?

Has the sensor under the pump had water on it? That makes them do strange things.
The modulation of the gas valve needs checking (corgi job) but the sensor(s) would be supect too.
Tony G may know better.
Back to top
 Alert Moderators
Agile

from United Kingdom

Joined: 26 Jun 2004
Posts: 24304
Location: London,
United Kingdom
Thanked: 191 times

PostPosted: Wed Jun 27, 2007 11:54 pm    Post Subject:
Reply with quote Thanks

It seems to me that he has described the correct CH operation and the only problem is what has already been suggested, a blocked plate HE.

Its easy to test that over the telephone, run a basin hot tap and see what temp the gauge goes up to. It should stabilise at about 55-60°C.

It it goes to about 70°C then there is some blockage in the primary side and if its much higher then it will need immediate attention.

Dr Margaret Busby OBE who was on R4 today has that problem with her boiler!

Tony
Back to top
 Alert Moderators
seegee

from United Kingdom

Joined: 27 Jun 2007
Posts: 2
Location: United Kingdom
Thanked: 0 times

PostPosted: Wed Jul 04, 2007 7:29 pm    Post Subject:
Reply with quote Thanks

Agile wrote:
It seems to me that he has described the correct CH operation and the only problem is what has already been suggested, a blocked plate HE.

Its easy to test that over the telephone, run a basin hot tap and see what temp the gauge goes up to. It should stabilise at about 55-60°C.

It it goes to about 70°C then there is some blockage in the primary side and if its much higher then it will need immediate attention.

Dr Margaret Busby OBE who was on R4 today has that problem with her boiler!
seegee- if the heat exchanger is the problem and the plate is mucky then what is best practice for its inspection and cleaning also how does the gas flame check itself when the demand reaches desired temperature-it cannot just turn off it must modify its output - is this checkable say a voltage to the flame control.
Tony
Back to top
 Alert Moderators
rob884

from United Kingdom

Joined: 14 Aug 2006
Posts: 2290
Location: London,
United Kingdom
Thanked: 2 times

PostPosted: Wed Jul 04, 2007 7:41 pm    Post Subject:
Reply with quote Thanks

seegee even at very low rate it can still cause the water to get too hot due to restriction. Just replace it. I wouldnt recommend a diyer to try and clean it.
Back to top
 Alert Moderators
gas4you

from United Kingdom

Joined: 23 Feb 2007
Posts: 14312
Location: Norwich,
United Kingdom
Thanked: 41 times

PostPosted: Wed Jul 04, 2007 7:43 pm    Post Subject:
Reply with quote Thanks

rob884 wrote:
seegee even at very low rate it can still cause the water to get too hot due to restriction. Just replace it. I wouldnt recommend a diyer to try and clean it.


1001 cleans a great big carpet, and all for half a crown icon_lol.gif

__________________
Dave
DRL Gas Services
Back to top
 Alert Moderators
Display posts from previous:   
  View previous topic :: View next topic  
Post new topic   Reply to topic    DIYnot.com Forum Index > Plumbing and Central Heating All times are GMT
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
Similar Topics   Replies   Views   Posted 
BIASI PRISMA 24SE Start Probs 11 180 Thu Sep 24, 2009 5:21 pm
pressure rising with Biasi Prisma 24SE 3 120 Sun Nov 30, 2008 12:10 pm
Biasi - Prisma 24se ( no hot water ) 4 540 Wed Nov 28, 2007 1:23 pm
No flame of my boiler, Biasi Prisma 24SE 8 420 Sun May 18, 2008 7:12 pm
Prisma bolier 24se pilot light keeps going out 2 100 Sun Feb 17, 2008 7:36 am



DIYnot
Find an Expert | Find a Supplier | Search DIYnot.com
My DIYnot | Advertising | Newsletter
DIYnot.com | How to... | @home | Wiki | Forum
By using this site you agree to our Terms of Service / Disclaimer.
Please read our Privacy Policy.