Posted: Fri Aug 24, 2007 10:11 pm Post Subject: Shower cable |
 |
|
Hi All, would 6mm cable on a 9 metre run using a 40 amp mcb, be sufficient for a 8.5kw shower? The consumer unit has a built in rcd. The cable is only buried in the wall for 2.5 ft, the rest is uncovered. (under bath and in the loft space not covered by insulation) |
|
Aardvark Avo

Joined: 25 Aug 2007 Posts: 27 Location: Somerset, United Kingdom Thanked: 0 times
|
Posted: Sat Aug 25, 2007 2:57 am Post Subject: |
 |
|
These are given directly from quote from books, as such I take no liability:-
8500/230 =37 amps
with reference to the electricians guide to building control
up to 7.2 kw =6mm
upto 9.6 kw =10mm
BS7671
method 2(buried in wall P210 same as method 1 current capacity)
If you also go by bs7671 regs p220 method 1, max cap 6mm 47 amps
my choice would be 10mm as I have guessed how cable is buried and if the cable was in thermally insulating wall only 34 Amps rated.
******Legally part p it should be fitted by registered installer*******
please understand I wish to cover myself while still answering your question  |
|
Steve