It was showing original fault as f4 which is a flow probe fault these have been changed but fault returns after a few hours the right hand thermister seems to b the problem but must be something else making this thermister fail
Insufficient bypass! Or flow through boiler
There is a spring bypass in the boiler that will open to divert some heat through plate hex, if however there is no bypass on system of not enough flow then the water goes through the plate too much causing the return temp to be higher than flow.
Also if too much heat in the main hex the "no flow" thermistor reading will be over 10 degrees more than the flow causing a "no flow " lockout too. As you are saying it's doing it after a couple of hours each time then that sounds like the problem.
Why not get ideal out as under warranty?
24 months I think on normal logic five years on plus. I would be taking flow and return temperatures. On a side note is the heating left on just now with the rads turned down? As I've seen that a lot just now as people do t like messing with clock. If so turn it to summer setting