... per what I keep saying, I'm not convinced that the person/persons who wrote those gas regulations understood anything much about electricity. As I've been implying, the statement ...
The purpose of equipotential bonding is to ensure the gas installation remains safe under electrical fault conditions
... makes little sense to me, since it seems to me that the opposite is the case. As I have said, the effect of bonding a gas pipe is that, under certain electrical fault conditions, extremely high currents could flow in the gas pipe, potentially leading to considerable local heating or even sparks in ther gas pipe, particularly in the vicinity of joints/unions. I would therefore have said that bonding a gas pipe does quite the opposite of "ensuring the gas installation remains safe under electrical fault conditions"!
As has been said, the gas pipework will almost always be connected to earth via the CPCs ('earth wires') feeding boilers, CH pumps and motorised valves etc., so the risk to which I refer already exists to some extent. However, adding bonding will, as far as I can see, make the situation appreciably less safe (gas-wise) by increasing the fault current.
If, as is commonly the case, the gas supply pipe does qualify as an extraneous-c-p then,
electrically speaking, bonding
is essential (to reduce the risk of electric shock), even if the result is to make the gas installation less safe.