4mm Radial Circuit

Joined
20 Feb 2007
Messages
41
Reaction score
0
Location
Devon
Country
United Kingdom
In a domestic environment is it ok to use 4mm T&E for radial circuits using a 32a MCB?

Standard rings would be a nightmare in this house.

Cheers
Nick
 
Sponsored Links
It's very worrying that you've chosen an electrician who doesn't know that - you should give very serious consideration to replacing him with someone actually competent to rewire your house...
 
Maybe 4mm 32a radials for down stairs, but in a gas CH house do you really need a 32a radial(s) upstairs ?

There's a certain staggered terrace design round here that makes it prudent to provide 2 x radials (front half and back half) of the 1st floor.

Due to ease of load 2 x 20a radials run in 2.5mm works well and keeps inside the 50m sq rules- whole floors run on 1 radial would be outside design due to floor footprint being >50m sq.
 
Sponsored Links
No its not alright, 32A radials need 6mm cable,

Even if the cable routes avoid any insulation?
When clipped direct, 4mm carries 37A. Length could be an issue though (~32M max).
You would also have to check that a 1.5mm cpc is sufficiently sized and thermally protected for the duration of a fault.
 
Don't think 1.5mm CPC is a problem with a 32A MCB, will be even less energy let through with an RCD. We see a 1.5mm CPC on a ring final all the time, on its own in the case of spurs.
iirc the only combination which was cause for concern was the 1mm CPC and 30A rewirable fuse found in some old ring final circuits.
 
Maybe i should have rephrased that better - method C which uses the same ratings as clipped direct in table 4D5.
 
How can you use method C, surely in the majority of house circuits (except garages and sheds etc) the only applicable methods are A or B. :confused:

How? Because the majority of installs will be method C.

Have a read of table 4A2, number 58 (page 264 of BS7671:2008)/
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Sponsored Links
Back