Adding a cpc

Joined
16 Jul 2007
Messages
14
Reaction score
0
Location
Manchester
Country
United Kingdom
Hello,
If a lighting circuit has been installed without a cpc in the CU.
But everywhere else in every switch and light there is a cpc.
Would it be alright to add a 2.5mm cpc in the CU and runnit to any switch or light?
Because I tried it with a wonder lead and I am getting a Zs on the lights.
Thanks in advance.
 
Sponsored Links
A separate earth core must be 4mm² unless it is mechanically protected.

Can't you run a new length of 1.5mm² t&e to the first junction box/ceiling rose?
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Sponsored Links
Back
Top