One of the walls in my living room only has 1 x 13amp double socket outlet in the corner. I would like to add some additional sockets further along the wall. Is this just a case of spurring off the existing socket or will I have to have new cabling run back to the consumer unit?
 
Sponsored Links
Hi, if you existing socket is proven to be part of the ring and does not have a spur taken from it already you could add 1x double 13a as a spur. If you require more than 1 additional socket you would have to extend the ring. If you want a bank of sockets for av kit you could spur a FCU of the ring and add as many sockets as you require from the LOAD side of the FCU the maximum load on all your new sockets would be 13a.


Regards,

DS
 