My boiler has just started to turn the heating on intermittantly even though it is set for just hot water the heating side been turned off anyone any ideas please
The Alpha C23 has a built in frost thermostat which brings the CH on if the primary thermistor thinks that the water is cold enough these are prone to becoming faulty but arent too expensiv, I would disconnect all external controls and the internal time clock if fitted and if it still comes on intermittantly it will most likely be the thermistor, this is however within the roomsealed chamber so you will have to call an RGI to get them to replace the thermistor for you
frost thermostat has been replaced and no further problems thanks ianmcd seems you didnt need to know what else was in the system unlike GRUMPY 45yearsagasman
Ha Ha glad to be of help Chopper I have only been a gas man for 32 years maybey when I get to 45 years I will be grumpy too, certainly if you ask my missus she will agree