Having said that, if I were a householder commissioning work to be undertaken by an electrician during the next few months, I would be very annoyed if, during that 'transition period' the electrician failed to inform me if (s)he was designing/undertaking work which (s)he knew would be non-compliant with the regs which would be in force in a few months' time. In that situation, I would have expected to have been appraised of the situation, so as to give me the option to ask for the work to be undertaken so as to be compliant with the (known) 'upcoming' regulations
Kind Regards, John
Can't see how any work complying with the volt drop requirements of today can fall foul of the reduced loop impedance values. If it does not comply with volt drop then it's just non compliant end of story.
When it dropped for a B32 MCB from 1.5Ω to 1.44Ω we did not have any problems as at 1.5Ω it was also 4% not 5% volt drop.
The problem as I see it is still accuracy of measurement. Without taking into account bunching, temperature and the corrections where volt drop can move from 18 mV/A/m to 16.5 mV/A/m when corrected just moving the readings by one digit on Ze and Zs readings and volt drop moves 0.35 volts so the calculations at best are +/- 0.7 volts.
Use a loop impedance meter twice and the reading can change by 0.02Ω so add that and one realises that +/- 2 volt error is possible. So until the calculated reading is 13.5 volt you really don't know if it's an accuracy issue or if the installation is really out of speck.
So looking again at final ring on a TN-S system then 1.39Ω Zs will just about fall into the volt drop requirement assuming Ze = 0.8Ω so in this case it could after the amendment fail but would be so close one in real terms could only advise that the ring final was at maximum length rather than say it's non compliant.
But if one looks as a shower supply at 45A then 0.9Ω with a TN-S incomer of 0.8Ω although in theroy 16 meter of cable (10mm²) can still be used I would say your right on the edge and in real terms disconnection times are more down to RCD than the MCB.
Although the regulations say we can't rely on just a RCD since the RCD is tested and we can't test a MCB I am more inclined to trust the RCD for rapid disconnection times.
As to industrial situation the reduced low voltage transformer is often provided with only a 12A trip (thermal only) on the incomer so with a line - earth fault at 230 volt in and 55 volt out then 50A can be delivered from a 16A socket before that 12A thermal tip will auto disconnect the supply. Compared with that the rest hardly seems to matter.