You might be in luck, then! what is the CSA of the extension lead cable?Ze was 0.09 when measured today, and this sub board and socket isn't very far from mains, so may be in luck!
Intellectually speaking, it would be nice to wait until (if) the problem recurs before changing to a Type D. If not, as I said, you'll probably cure it with the Type D without ever having any insight into the 'why'. However, expediency, rather than intellectual satisfaction, may well be the name of the day!
Mind you, a D40 is a bit 'frightening' since it needs 800A for a magnetic trip - one might even argue that it's 'hardly worth having'! What upstream OPDs are there?
Kind Regards, John