    I have a Baxi 105e and several times a day it will kick in (fire up the boiler but not the pump). It'll just sit there burning gas, heating the water in the boiler, not pumping with no demand for hot water or central heating.
    The raidiators will eventually start to heat up as the water heats up.
    This can be stopped by turning on and off a hot tap, it will then start again a bit later on.

    Has any one got any suggestions/experiences with this?

    Thanks

    Andrew
     
  2. Dan_Robinson

    Joined:
    1 Jul 2007
    Messages:
    33,983
    Thanks Received:
    5,770
    Location:
    Hertfordshire & London
    Country:
    United Kingdom
    Can't remember if these have a preheat.


    If you run a bath do any rads start to warm up?

    If the answer is yes to both, then you have a faulty diverter valve.
     
  3. 45yearsagasman

    Joined:
    14 Mar 2010
    Messages:
    5,281
    Thanks Received:
    907
    Location:
    Norfolk
    Country:
    United Kingdom
    The 105e instant does have a preheat. If your boiler is this model then the preheat can be turned off on the control panel.
     
  4. andy74rew

    Joined:
    8 Sep 2012
    Messages:
    2
    Thanks Received:
    0
    Location:
    Newcastle upon Tyne
    Country:
    United Kingdom
    There isn't a per-heat function. The boiler sitting there with no demand at all will just kick into life and just start burning gas for the hell of it. The pump doesn't start. There aren't any fault codes.
     
  5. stew1

    Joined:
    25 Sep 2011
    Messages:
    12
    Thanks Received:
    3
    Location:
    Durham
    Country:
    United Kingdom
    the symptoms you describe should be not be possible the pump is proven by a microswitch which must be made before the boiler can ignite
     
  6. Agile

    Joined:
    26 Jun 2004
    Messages:
    55,386
    Thanks Received:
    3,638
    Location:
    London
    Country:
    United Kingdom
    It sounds tome like an intermittently faulty DHW demand switch!

    Tony Glazier
     
  7. Dan_Robinson

    Joined:
    1 Jul 2007
    Messages:
    33,983
    Thanks Received:
    5,770
    Location:
    Hertfordshire & London
    Country:
    United Kingdom
    sounds to me like the op is making assumptions.

    if the burner is firing for more than a few seconds without the pump running the boiler will be banging and clattering. the rafs wouldn't be heatimg up, amd it will overheat giving the respective lockout indication.
     
  8. gas112

    Joined:
    27 Oct 2009
    Messages:
    9,317
    Thanks Received:
    2,354
    Country:
    United Kingdom
    The pump will be running otherwise the boiler would sound like someone hitting it with a hammer .
    Choice of 2 faults microswitch or pin sticking on divertor after HW demand or the in built frost stat is faulty
     