BAXI COMBI 105 HE

Joined
7 Nov 2007
Messages
2
Reaction score
0
Location
Derbyshire
Country
United Kingdom
Hi I have a baxi that has a strange fault the boiler fires ok and runs in the heating mode for about an hour then it goes out with the fault light looking towards an air /fan fault. if i reset using the switch it fires up and runs for about another hour give or take. then goes out
i have looked at the pressure switch and it seams to be working
has anyone else had this one

any help would be appreciated

Thanks :cry:
 
Sponsored Links
Yep loadsa times. PCB usually needs replacing. 248074 , replaced by 5112380.
 
thanks For that Chris any way of checking for sure before the big cash handover ?
 
If youhave an analogue voltmeter, put it on the fan terminals on the pcb. If you get a little pulse when the fan should be starting, that's a dead-pcb "signature".

Obviously if it says faulty XYZ then it could always be telling the truth!
 
Sponsored Links
Beware this is a HE boiler and will already have a 5112380 pcb fitted. Venturi ,aps and tubes need to be checked first.
 
PB67";p="735631 said:
Hi I have a baxi that has a strange fault the boiler fires ok and runs in the heating mode for about an hour then it goes out with the fault light looking towards an air /fan fault.


Hi PB67,

I had a new system about 2.5 years ago and it has started to display the same fault. What was the solution?

Thanks.
 