Volex VX9990 is rated at 25A
As I said, where will you find it stated that the 'rating' of (the terminals of) a '13A Socket' is at least 32A - I can't say I've ever seen it.
Except for those who are obseessed with 'ratings' and MIs, this is all a bit academic. I have one of these things in my hand, and it's quite obvioulsy at least as capable as a 30A connector block of satsifactorily connecting two conductors carrying up to 32A.
You can say that again.Volex VX9990 is rated at 25A
Having looked at the one in my hand, that certainly doesn't surprise me - but where did you find that? I couldn't on the Electrium/Volex website.Volex VX9990 is rated at 25A
My take on that whole saga is that a 13A socket is designed to receive a 13A plug. ... And likewise, a 13A flex outlet plate is designed to connect (up to) 13A flex. And a 13A FCU is designed to take 13A on the load side.
http://www.discount-electrical.co.u...outlet-frontplate-with-bottom-cable-entry-25aHaving looked at the one in my hand, that certainly doesn't surprise me - but where did you find that? I couldn't on the Electrium/Volex website.Volex VX9990 is rated at 25A
Kind Regards, John.
Hmmm - so it's them we need to ask where they got it from, then. As I said, on the manufacturer's website, it's described as a "13A Flex Outlet Plate", with no other mention of current rating.http://www.discount-electrical.co.uk/product.php/2339805/volex-vx9990-white-moulded-flex-outlet-frontplate-with-bottom-cable-entry-25aHaving looked at the one in my hand, that certainly doesn't surprise me - but where did you find that? I couldn't on the Electrium/Volex website.Volex VX9990 is rated at 25A
My take on that whole saga is that a 13A socket is designed to receive a 13A plug. ... And likewise, a 13A flex outlet plate is designed to connect (up to) 13A flex. And a 13A FCU is designed to take 13A on the load side.
I don't think anyone would argue with any of that. However, the point is that the quibbling here was about whether or not the terminals on a flex output plate were 'rated' for the 32A which theoretically could be flowing through the conductors of the final circuit (ring or radial) into which is was connected. Exactly the same consideration applies to the 13A sockets and FCUs you mention, but where have you seen it stated that the supply-side terminals are 'rated' for the 32A which could be flowing through coinductors connected to them?
In other words, my point was that, although the load side of a socket or FCU is rated at 13A, that obviously doesn't mean that the accessory cannot be wired into a '32A circuit'!
Kind Regards, John.
I think the only thing you're missing is that everyone is being ultra conservative/cautious and assuming the worst possible case scenario ... if the circuit were 'fully loaded' and the entire load was concentrated very close to one end of the ring, then the current in one leg of the ring could 'approach' 32A. In reality, of course, the design assumption (given a good design) is that the current will not exceed 20A in any part of the ring, and I'm sure that's nearly always the case in practice.[I'm wondering why everyone is thinking that 32 A is flowing through the conductors? (i.e. through the OPs connection block) .... The current through one leg of a ring final is not going to be 32 A - or am I missing something??
Indeed - although, to be fair, BS7671's concept of current carrying capacity includes an implicit assumption that a cable can cope with 1.45 times it's tabulated CCC (e.g. 29A for a cable with a tabulated CCC of 20A, using the installation method in question) for at least one hour - so one could argue that terminals should be capable of also coping safely with that current.If you read 433.1.5 the current carrying capacity for tha cable for ring final circuit must not be less than 20A, so it stands the reason that the terminals should have at least the same rating i.e 20A
I'm sure that's right, and not only for the reason you give. As I've said before, I confess that I take 'current carrying capacity' of terminals with a large pinch of salt - as far as I'm concerned, what matters far more is the conductor accommodating capacity. The accessory we were discussing has terminals 'rated' to take 3 x 2.5 mm² cables, and that's good enough for me.So based on this if your terminals are rated at 20A you are going to be OK.