I was hoping someone could give some advice about our problem.
2 weeks ago, our Valliant boiler started losing pressure, approximately 1 bar every day. I switched it off and isolated the return and flow using the valves underneath the boiler, but the pressure kept dropping at the same rate. Hence the assumption was boiler problem, not system leak.
We've got BG boiler cover, so gave them a call. They isolated the boiler the same way to double check - boiler still losing pressure. So they investigated further - bags placed over condensate and pressure relief pipe to catch water (nothing there). They found water inside a container in the boiler - this led to them replacing the heat exchanger. But pressure still dropping (same rate).
So, boiler completely disconnected and capped off (return and flow, mains supply and hot and cold feeds, but not gas supply). Pressure held perfectly.
Before reconnecting, the expansion vessel was noted to be quite flat, so this was pumped (but they stated this was unrelated as pressure was not rising with heating on).
Boiler now reconnected, but is still losing pressure.
So, BG say it's a system leak. Okay, but why is there pressure loss in the boiler when we use the isolation valves under the boiler? BG say those valves definitely hold water as they were used when disconnecting the boiler - however BG suggest that they 'can hold water, but perhaps not pressure'. That doesn't makes sense to me
Before we start ripping up flooring looking for a leak, can anything think of a reason that may have been overlooked? Is it possible for the isolation valves to 'not hold pressure' but happily 'hold water'? Is there 'something' different when using isolation valves compared to completely disconnecting and capping off return and flow pipes?
Any thoughts, however obscure, would be much appreciated!
2 weeks ago, our Valliant boiler started losing pressure, approximately 1 bar every day. I switched it off and isolated the return and flow using the valves underneath the boiler, but the pressure kept dropping at the same rate. Hence the assumption was boiler problem, not system leak.
We've got BG boiler cover, so gave them a call. They isolated the boiler the same way to double check - boiler still losing pressure. So they investigated further - bags placed over condensate and pressure relief pipe to catch water (nothing there). They found water inside a container in the boiler - this led to them replacing the heat exchanger. But pressure still dropping (same rate).
So, boiler completely disconnected and capped off (return and flow, mains supply and hot and cold feeds, but not gas supply). Pressure held perfectly.
Before reconnecting, the expansion vessel was noted to be quite flat, so this was pumped (but they stated this was unrelated as pressure was not rising with heating on).
Boiler now reconnected, but is still losing pressure.
So, BG say it's a system leak. Okay, but why is there pressure loss in the boiler when we use the isolation valves under the boiler? BG say those valves definitely hold water as they were used when disconnecting the boiler - however BG suggest that they 'can hold water, but perhaps not pressure'. That doesn't makes sense to me
Before we start ripping up flooring looking for a leak, can anything think of a reason that may have been overlooked? Is it possible for the isolation valves to 'not hold pressure' but happily 'hold water'? Is there 'something' different when using isolation valves compared to completely disconnecting and capping off return and flow pipes?
Any thoughts, however obscure, would be much appreciated!