Boiler no longer working after power cut

Joined
22 Sep 2006
Messages
39
Reaction score
0
Location
Middlesex
Country
United Kingdom
I have a Gloworm Fuelsave compleheat 55
The power cut happened last night and now this mornig the boiler won't fire up, there is no pump or fan and the ch low pressure warning light is on.

I have tried the reset button, checked the fuse on PCB, I tried lowering the pressure then refilling, switching of & on numerous times, a few mild taps ont he pressure switch but alas I can't get it going.

Any suggestions please?
 
Sponsored Links
If the boiler is registering low pressure then it will presumably be holding the boiler off.

I recommend increasing the pressure to 1.8 bar and see if that will bring it on again but it may take several hours to restore.

The inlet to the LP switch is probably blocked and may have to be cleared/unblocked.

I should not suggest it except for a short test but you could join the two wired to the LP switch together and that will hopefully bring the boiler on to prove thats why its stopped.

Tony
 
Thanks Tony, yep I did try increasing the pressure to 2 bar but it still didn't do anything , I'll try the short.
 
Sponsored Links
ok the short did solve the problem, I phoned Glorworm first and made sure it was ok and they were really helpfull.
Gona order a new Water pressure switch. it seems not to be working, I took it out and it seems to have quiite a bit of sludge in there maybe it's time to do a flush.
LOL now I'll have to find out how to do that as well!
 