It appears that BS 4293 is a standard for RCDs.
Was there an overcurrent protective device in series with the RCD?
If so, the details of this device should be used to ascertain the maximum permissible Zs for the circuit.
If not, the supply needs switching off, and given a code 1 on your report.
The rcd was fed directly from a 100mA time delay RCCB. Let me enlighten you on the subject.
Meter tails via meter into a metal MK dual dist board 100mA RCCB main switch.
Some plonker has retro from the bottom of the 100mA tails feeding 2 banks of BS3871's and directlt from the 100mA main switch is feeding a 30mA rcd that in turn is supplying power to an isolator for the stage lighting