No, but 2 x 2.5mm² does equal 1 x 5mm²Urm, 2x 2.5mm cores does not equal a 5mm core, its far less than that......
If the OP did actually mean he had 2.5mm diameter cores he'd probably have 6mm² cable, or an old imperial 7/.036.
No, but 2 x 2.5mm² does equal 1 x 5mm²Urm, 2x 2.5mm cores does not equal a 5mm core, its far less than that......
No, but 2 x 2.5mm² does equal 1 x 5mm²Urm, 2x 2.5mm cores does not equal a 5mm core, its far less than that......
If the OP did actually mean he had 2.5mm diameter cores he'd probably have 6mm² cable, or an old imperial 7/.036.
I would correct you but what does it mean?OK maybe I am confused then. I thought 2x 2.5mm² cores would equal approx. a 2.5 x 5mm² core, so half of a 5mm² core? Happy to be corrected.......
I would correct you but what does it mean?OK maybe I am confused then. I thought 2x 2.5mm² cores would equal approx. a 2.5 x 5mm² core, so half of a 5mm² core? Happy to be corrected.......
Oh yes - you cannot equal approx.
I would correct you but what does it mean?OK maybe I am confused then. I thought 2x 2.5mm² cores would equal approx. a 2.5 x 5mm² core, so half of a 5mm² core? Happy to be corrected.......
Oh yes - you cannot equal approx.
Your attitude is not helpful. If you are going to reply please make it something constructive.
No, but 2 x 2.5mm² does equal 1 x 5mm²Urm, 2x 2.5mm cores does not equal a 5mm core, its far less than that......
If the OP did actually mean he had 2.5mm diameter cores he'd probably have 6mm² cable, or an old imperial 7/.036.
The analogy of placing two tiles of equal size is not quite correct. If you were to unwind the strands of two 2.5 conductors and then rewind them into 1 conductor then the cross sectional area should equal 5mm. If I had two dustbin lids each of which covered a metre square then between them they cover 2 square meters.
Everything really depends upon what loads you intend to plug into those 4 double sockets. There is no immediately available figure for the current-carrying capacity of 5.0mm² SWA (2x2.5mm², doubled up), since CCC is not directly proportional to conductor CSA, but it will presumably be at least as high as 2-core 4mm² SWA, which would allow you 43A if buried. With only 10-12 metres, voltage drop is not likely to be a limiting factor. What is going to be feeding this cable, and what arrangements for RCD protection of the garage circuits will you have?I will be installing 3 internal double 13a sockets and 1 external double socket. I will have two fluorescent light fittings and one outside LED light on a PIR. I may fit some heaters on a frost protection stat. As mentioned above 2.5 mm wouldn't give me much so I was intending to use the 4 core as a single phase with bunched or paired cores and either run a separate 6 mm conductor or use the steel wire conductors as the earth.
The armour of the SWA would probably be adequate to act as CPC for the "5mm²" cable, but if you have a requirement for main protective bonding in the garage, you may well need to run a 10mm² cable (from house Main Earthing Terminal to garage) for that purpose. How do you intend to deal with earthing arrangements (and bonding if required) in the garage?
Kind Regards, John
The analogy of placing two tiles of equal size is not quite correct. If you were to unwind the strands of two 2.5 conductors and then rewind them into 1 conductor then the cross sectional area should equal 5mm. If I had two dustbin lids each of which covered a metre square then between them they cover 2 square meters.
...
So I wasn't quite correct, but I was exactly correct?
The analogy of placing two tiles of equal size is not quite correct. If you were to unwind the strands of two 2.5 conductors and then rewind them into 1 conductor then the cross sectional area should equal 5mm. If I had two dustbin lids each of which covered a metre square then between them they cover 2 square meters.
...
So I wasn't quite correct, but I was exactly correct?
My apologies!!
My heads a bit frazzled after chasing an Arc Suppression Fault in the pouring rain and then trying to find a HV earth fault which broke down at 8kv but we cannot find!! Went to work at 7 this morning and rolled in at 11 tonight!!
Re read your post saw we were on the same page.
I have a great deal of sympathy with him. Apart from being picky about "equal approximately" vs "approximately equal", I agree that what you wrote made no sense at all, so much so that I couldn't even try and guess what you might have meant.I would correct you but what does it mean?OK maybe I am confused then. I thought 2x 2.5mm² cores would equal approx. a 2.5 x 5mm² core, so half of a 5mm² core? Happy to be corrected.......
Oh yes - you cannot equal approx.
Your attitude is not helpful. If you are going to reply please make it something constructive.
Nobody has said it doesI think the confusion is related to the fact that doubling cross sectional area does not double current carrying capacity
No skin effect at 50Hz.(surface area, skin effect, yadayada).
If you say so.Brain not in gear syndrome.
Nobody has said it doesI think the confusion is related to the fact that doubling cross sectional area does not double current carrying capacity
No skin effect at 50Hz.(surface area, skin effect, yadayada).