the only faults they discovered were the bonding and socket on skirting.
What exactly is "wrong" with the bonding?
The socket on the skirting board is easy to fix if someone is going to be that picky.
it would mean going through concrete floors etc as he insisted it must be next to the gas meter and not the pipes under the floorboards.
Photos of what bonding you have, and where, would be useful.
If you want to use the site's own photo library provision you'll find the instructions here:
//www.diynot.com/network/DIYnot/albums/67/180
To get photo(s) to appear in your post you need to do all 11 steps.
Or in a fraction of the time it takes to go through that convoluted process you could use an image hosting site such as
http://www.postimage.org
The spark said he is not allowed to put in a new CU unless everything it is connected to meets the regs - i.e. the whole house.
He is obviously not thinking clearly.
If that were true then no electrician could ever replace a CU without half-gutting the house first, or ignoring every single existing cable and doing a complete rewire.
To be sure that everything connected to it complies with the regulations he would have to dig out the plaster over every cable in the walls, and lift floor and/or remove ceilings so that he could check every bit of every cable to ensure that:
They all run in the right places.
They are the right size from end-to-end (no undersized sections).
There are no concealed screwed joints.
There is no unrepaired damage.
There is no missing sheathing.
He is aware of all the thermal insulation and grouping etc factors which affect their current carrying capacity.
Nobody does that. He was not suggesting that he had to do that. He just wasn't thinking.
But of course challenging him on this isn't going to work - at best you'll get a resentful electrician doing things under protest, and that won't end well. You need to kick him into touch and get one who understands that when he signs an installation certificate for the replacement of a CU it is the work of replacing the CU which he is certifying was compliant with the regulations, not the entire installation.
But that will include fixing the problems with the bonding (whatever they are - hence the request for photos).
Very early on in the Regulations, in the Fundamental Principles, it says this:
No addition or alteration, temporary or permanent, shall be
made to an existing installation, unless it has been ascertained
that the rating and the condition of any existing equipment,
including that of the distributor, will be adequate for the altered
circumstances. Furthermore, the earthing and bonding
arrangements, if necessary for the protective measure applied
for the safety of the addition or alteration, shall be adequate.
Separately, I was under the impression that the protection the bonding gives is minimal compared to the protection a new RCD CU gives?
If your bonding is inadequate that has to be resolved.