Central heating

Joined
15 Feb 2005
Messages
13
Reaction score
0
Location
Carmarthenshire
Country
United Kingdom
I recently had to remove a radiator to tile behind it. I have been battling for 2 days now to get them all to warm up. I have bled buckets of water from the two remaining ones untill they warm up. The hot water does get to them but they just cool down again. 80% of the other ones are warming up nicely after several buckets of water was bled from them.

Am I doing something wrong? Please help, only two stubborn ones to sort out. It is not a closed system and is gas.

Thanks for any help
Gosso
 
Sponsored Links
Have you tried to close the valves of all the radiators so only the two suspect ones are active? if not, try that.. If the rads then work fine, you will need to balance the rads...

i.e. The rads are on a loop and the rads closest to the boiler in the loop will be most efficient so the valves don't need opening as much as they would for the last ones in the loop.
 
yep thats done the trick! Is this common to balance the system after removing a radiator?

cheers for the help guys
 
The rads need to be balanced only if you fiddle around with the valves on the rads...

Really once they are balanced the valves on the rads shouldn't be touched and heating control should be done via the thermostat.

...and then, when you decide to remove a rad and replace it, it should just be a case of remembering how many turns the valves were opened to before removal.
 