I would like to go for Viessmann, but it will all depend on what engineers can do, etc.
Ask Viessmann for names of installers who can give a five year warranty.
My idea was to replace radiators at the same time as the boiler (and removing hot water tank in the airing cupboard + tanks in the loft). The radiators are over 20 years old. Would you replace them or leave them as they are?
If you replace them, you can at least make sure they are correctly sized.
I know, I have to do some calculations on what sizes are needed for the room
The correct way is to use a heat loss program such as Stelrad Stars. But you could get a reasonably accurate idea by allocating the total boiler output to each room as shown below You have to deduct 2kW from the calculated boiler size, as this is the allowance for the hot water cylinder.
For example:
Boiler output = 18kW - 2kw = 16kW for heating
Total floor area = 80m²
Requirement = 0.2kW per m²
Room area = 12m²
Heat required = 12 x 0.2 = 2.4kW radiator
You can find the output of your existing rads from a manufacturer's catalogue. There is very little difference between manufacturers for the same size and type of product so the
Stelrad Elite Catalogue is as good as any. For unusual rads use the
Guide to Radiator Outputs
If you want to have the boiler condensing as much as possible the return temperature needs to be below 55°C. Now rad outputs are measured under defined conditions: Flow temp = 75C, Return temp = 65C, Room temp = 20C. If you alter any one, the output will change. You have to allow for this when sizing your rads. So for flow = 75C, Return = 55C, Room =21C , you will have to oversize the radiator by 20%. This is because the rad will be giving out less heat than the mfrs literature says. So, if the size of the rad works out at 2.4kW, you install a 2.88 rad (say 3kW). You do
not increase the boiler size by 20%!
You said earlier that the house was built in 1988. In that case it is unlikely to have any cavity insulation. Check out the Grants site I mentioned in a previous post.