Evening all.
The lights in my house have been wired using the junction box method and the cpc stops at the junction box. I understand that in theory the last junction box before the light pendant is effectively the same as the loop-in ceiling rose is using that particular method ,and the cpc does indeed stop at the ceiling rose and not at the end of the flex. But with the cable from the JB to the fitting being up to 4 metres long, is it ok to have no cpc running with it to the fitting?
Thanks
The lights in my house have been wired using the junction box method and the cpc stops at the junction box. I understand that in theory the last junction box before the light pendant is effectively the same as the loop-in ceiling rose is using that particular method ,and the cpc does indeed stop at the ceiling rose and not at the end of the flex. But with the cable from the JB to the fitting being up to 4 metres long, is it ok to have no cpc running with it to the fitting?