Afternoon all
Tested CU today which had 2.5Vac L & E and L & N in load side of CU with main isolator open. All MCBs were open also. Load side L to supply side L was 50Vac or so.
When closing the MCBs the potential difference dropped to 0 and the load L to supply L went to a normal 245Vac.
Is this expected behaviour?