Hi folks, have to connect a 13.8Kw oven in a domestic property.
13.8/230 = 60A
Checking the regs it says 10A + 30% of remainder so;
10A + (50 x 0.30) = 25A
there is no socket!!!
This just does not seem to ring true, it suggests that 4mm and 32 A MCB would suffice.
I was thinking more like 10mm and an 60A, after all it is bigger than most showers!!! The run is under 10m
When the whole thing is running on christmas day..........
13.8/230 = 60A
Checking the regs it says 10A + 30% of remainder so;
10A + (50 x 0.30) = 25A
there is no socket!!!
This just does not seem to ring true, it suggests that 4mm and 32 A MCB would suffice.
I was thinking more like 10mm and an 60A, after all it is bigger than most showers!!! The run is under 10m
When the whole thing is running on christmas day..........