Hi guys, I have LP722 controller, which was working fine until this autumn, but now it has developed a fault-it will only turn on either hot water OR heating, and I have to play with the control buttons to get either working. Both will not work at the same time, although bot red indicators will be on. The system was absolutely fine for the past 5 years. I`m thinking that a relay possibly gone in the unit, am I wrong?

Thanks in advance for any advice!
 
Sponsored Links
If the controller has failed then its best to change it. Before doing that, check that the fault is not on a system zone valve first. Do a bit of fault finding before throwing parts at it.
 
If the controller has failed then its best to change it. Before doing that, check that the fault is not on a system zone valve first. Do a bit of fault finding before throwing parts at it.
Pete, thanks for the reply. The problem is that I have very brief knowledge of CH and HW systems. Where normally that valve is, and what does it look like (-ish)?
Thanks
 
Sponsored Links
It depends on the type of system you have. I would be looking for one of these on your system. At this stage it is only guesswork as your system type is not clear. Boiler make/model would also help. ]
I have Range Tribute HE dual coil boiler, Honeywell F8 valves(2), and Grundfos UPS (which I presume is pump). It also has solar water heating panel system connected to it.

Thanks for your help.
 