Hi all
Just wondered if I could rack your collective brain about this one. Sorry it's lengthy, but might have implications for many of you!
Recently tested out my system and Ze (External Loop Impedance) came in at 1.01ohms. I'm on a TNS so the regs state the max permissable is 0.8. In addition, my next door neighbours share my earth, so they were also 'at risk' (In fact I have a suspicion that the Ze was only obtained because they have bonding to their gas/water pipes - I don't)
So I phoned the supply company, who came out to retest and just confirmed what I had found (suprise, suprise!). However, on speaking to their engineer, he said that
1. He didn't think this was an unsafe reading (despite the fact that the regs say otherwise, which he admitted)
2. As the company had not supplied the earth, it was not their responsibility to correct it anyway. (When I asked how he knew it wasn't their's, he just said - that's not how we'd do it)
His advice to me was to put up with the reading or install an earth rod in my garden (I live in central London and doubt whether I'd get any better Ze). I also don't want my lights on and RCD
This is not the first time I have come across this - and it's p*ssed me off as basically I think the supply companies are passing the buck either back to the consumer or to their electrician. Is this as a result of privatisation/deregulation??
Has anyone else encountered this? How did you get it resolved (if at all??)
SB
Just wondered if I could rack your collective brain about this one. Sorry it's lengthy, but might have implications for many of you!
Recently tested out my system and Ze (External Loop Impedance) came in at 1.01ohms. I'm on a TNS so the regs state the max permissable is 0.8. In addition, my next door neighbours share my earth, so they were also 'at risk' (In fact I have a suspicion that the Ze was only obtained because they have bonding to their gas/water pipes - I don't)
So I phoned the supply company, who came out to retest and just confirmed what I had found (suprise, suprise!). However, on speaking to their engineer, he said that
1. He didn't think this was an unsafe reading (despite the fact that the regs say otherwise, which he admitted)
2. As the company had not supplied the earth, it was not their responsibility to correct it anyway. (When I asked how he knew it wasn't their's, he just said - that's not how we'd do it)
His advice to me was to put up with the reading or install an earth rod in my garden (I live in central London and doubt whether I'd get any better Ze). I also don't want my lights on and RCD
This is not the first time I have come across this - and it's p*ssed me off as basically I think the supply companies are passing the buck either back to the consumer or to their electrician. Is this as a result of privatisation/deregulation??
Has anyone else encountered this? How did you get it resolved (if at all??)