At 20:00 on a Saturday with NCIS on the box? You must be kidding
I'll see what I can do.
t is the time taken to disconnect the fault current for the particular device in use (from the time/current characteristics in Appendix 3).
You may need to refer to manufacturers data for time less than 0.1s.
It raises an interesting point though, and that is if you strike a nail through a cable at or near the consumer unit, assuming we were protected by MCBs then the cable would be very toasty . You may not see a fault level high enough not to trip the MCB before enough energy is let through, but it could happen.
mfarrow";p="1469766 said:Blimey - a 16mm earth in addition to the CPC? Oh well you've read the thread so we can't really help you further. By the way the boiler pipes will not require any bonding unless that's the point where the gas comes into your house.
No, I'm still listening.
I only thought it a good idea to bond those pipes as they were near the CCU.
If I don't need to, will no additional earthing be required ? the 6mm CPC will be enough ? BTW, I do have a 100A cut out.
Surely putting a nail through a cable between the line and neutral is the same as putting a cable between the L & N terminals?Your example differs to the potential problem you highlight somewhat!
mfarrow";p="1470305 said:If you mean do I have any examples of where the fault level was high enough for the MCB not to trip in time, then unfortunately I do not. It might not ever happen in real life, I'm just highlighting a potential problem
Yes, that's what I mean't.