Generally a 32A circuit is adequate for all but the very largest range style cookers. Certainly adequate for this model, although the manufacturer instructions specify a 45A circuit. The instructions are incorrect according to BS7671 (aka "the wiring regs") because they haven't taken diversity into account.
Traditionally 30/32A cooker circuits have always been installed with 6mm2 cable, but this is a legacy allowance for rewireable fuses, and in most circumstances 4mm2 is actually sufficient. Unless the run is very long or the cable is routed through thermal insulation, for instance.
Maybe I "haven't lived", but I have to say that I've never come across any domestic cooker that would not be OK on a 32A circuit. With the usual allowance for diversity for a cooking appliance, such a circuit could support a cooker with a maximum ('everything energised simultaneously') load of 83.33 A (about 19.17 kW at 230V).
Maybe I "haven't lived", but I have to say that I've never come across any domestic cooker that would not be OK on a 32A circuit. With the usual allowance for diversity for a cooking appliance, such a circuit could support a cooker with a maximum ('everything energised simultaneously') load of 83.33 A (about 19.17 kW at 230V).
There certainly aren't many, and those few that exist are in the £3500+ bracket, but Smeg for example do an absolute beast of a 3 oven, 5 induction ring range style cooker that claims to be just over 19.5kw.
so you just need a suitable cable from the wall connector into the cooker. This one is flexible and resistant to the heat and potential greease splatters. As you order it per metre, 2m would usually be ample to roll out the cooker when you need to clean behind it. There may be a local supplier handy to you.
There certainly aren't many, and those few that exist are in the £3500+ bracket, but Smeg for example do an absolute beast of a 3 oven, 5 induction ring range style cooker that claims to be just over 19.5kw.
It's just as well that some people do understand the concept of diversity because, if not, they would probably conclude that the requirements of a "19.5 kW cooker" actually exceeded the property's 'total available supply' (most commonly 80A - about 18.4 kW at 230V)
If you need to find a tradesperson to get your job done, please try our local search below,
or if you are doing it yourself you can find suppliers local to you.
Select the supplier or trade you require, enter your location to begin your search.
Please select a service and enter a location to continue...
Are you a trade or supplier? You can create your listing free at DIYnot Local