cross said:
I am seeking some clarification on what the neutral actually does...
I have heard the neutral is considered to be at zero volts.
I have also heard that the neutral carries current back to the source, therefore completing the circuit.
If this is true, how does the current travel along the neutral if there is no voltage forcing it along??
Current travels along a conductor because there is a potential difference between the two ends of the conductor.
In the case of conductors used to supply power, this potential difference will be very small.
When you say "the neutral is considered to be at zero volts", the "zero volts" to which you are referring is the potential difference relative to earth.
In fact, whenever there is a current flowing in a conductor, it does not have one single potential; there will be a potential gradient along the conductor. This can be measured as a potential difference between the two ends of the conductor.
The end of the neutral conductor at the substation may well be at zero volts relative to earth.
However if there is any current flowing in the circuit, then at any other point on the neutral conductor the potential will be non-zero.
Consider the live and neutral conductors between the substation and your house.
Say they have a resistance of 0.1 ohms.
Say the supply voltage is 232 volts at the substation.
Say your house is drawing 10 amperes.
According to Ohm's law, the potential difference is equal to the product of the current and the resistance.
Any current flowing through one conductor will be matched by an equal and opposite current flow in the other conductor.
So each of the supply conductors will have a potential difference between the ends of 10 x 0.1 = 1 volt.
It is this 1 volt potential difference between the ends of the conductor that drives the current through it.
Both the live and neutral conductors are in the same situation; they have the same potential difference across them, so current is driven through them in the same way.
Considering the neutral conductor, the end at the substation will be at zero volts relative to earth, but the end at your house will be at one volt relative to earth.
Similarly for the live conductor, the end at the substation will be at 232 volts relative to earth, but the end at your house will be at 231 volts relative to earth.
The "supply voltage" as measured at your house will be the potential difference at the house which will be the expected 230 volts.
(As you can see, the "voltage" at the house will be dependent on the current being drawn, and the resistance of the supply cables. The current will vary according to demand, and the resistance will vary according to the distance between any given house and the substation. So pretty much everyone will see a different "supply voltage" and it will also vary between different times of day.)