Does anyone have experience of intermittent faults that trip an RCD, that are caused by influences external to the house?
I have an elderly couple who had a new consumer unit fitted about 2 years ago (not by me - needless to say no cert although it does appear to have been installed more or less correctly).
The cutout is a little unusual compared to the ones I normally see as it had two separate incoming cables, Neutral and Phase, which are both clamped to provide a TN-S.
The clamps may look like a DIY install, but I suspect not as I see a lot of TNS done this way around here.
The problem is that the RCD is regularly tripping for no obvious reason. They noticed recently that when the neighbour used her hedge trimmer it tripped 3 times in 20 minutes.
I only had chance to have a quick look on Friday and I checked all the circuits IR (fine), ring continuity (Fine except for one high P-P which I will resolve but I don't think is connected to the fault) and the RCD (ramp test tripped at 27mA and I/5I tests all fine).
The installer came back a year or so ago and moved the cooker circuit to the non RCD side to try to eliminate this fault, which it failed to do. All that is left on it is a new shower install and two RFCs.
I am going back to check out a couple of appliances (Fridge, Freezer) which could possibly be causing the fault, but they are not particularly old.
I have run into enough coincidences to know you can not rely on things like noticing a neighbour using a hedge trimmer, but has anyone run into ways that the external supply can cause random RCD tripping? I am sure I have heard something about it but couldn't find an exact match with a search. The earth does not seem to be shared via a split cut out, though I haven't had access to next door to check yet. However, the neighbours supply is apparently on the opposite wall to this one so the earths could well be as good as linked underground.
I realise that RCDs in theory should only monitor the downstream supply, but is there a way that something 'upstream' could cause frequent tripping, or should I forget that and concentrate inside?
On a possibly related note, the resistance of Neutral to Earth external to the supply was about 0.6. Obviously TN-C-S wuold have a low resistance, but TN-S? I am guessing that they tie the outer sheath to earth at the same point as they tie the Neutral to supply for PME?
Any suggestions welcome
Gavin
I have an elderly couple who had a new consumer unit fitted about 2 years ago (not by me - needless to say no cert although it does appear to have been installed more or less correctly).
The cutout is a little unusual compared to the ones I normally see as it had two separate incoming cables, Neutral and Phase, which are both clamped to provide a TN-S.
The clamps may look like a DIY install, but I suspect not as I see a lot of TNS done this way around here.
The problem is that the RCD is regularly tripping for no obvious reason. They noticed recently that when the neighbour used her hedge trimmer it tripped 3 times in 20 minutes.
I only had chance to have a quick look on Friday and I checked all the circuits IR (fine), ring continuity (Fine except for one high P-P which I will resolve but I don't think is connected to the fault) and the RCD (ramp test tripped at 27mA and I/5I tests all fine).
The installer came back a year or so ago and moved the cooker circuit to the non RCD side to try to eliminate this fault, which it failed to do. All that is left on it is a new shower install and two RFCs.
I am going back to check out a couple of appliances (Fridge, Freezer) which could possibly be causing the fault, but they are not particularly old.
I have run into enough coincidences to know you can not rely on things like noticing a neighbour using a hedge trimmer, but has anyone run into ways that the external supply can cause random RCD tripping? I am sure I have heard something about it but couldn't find an exact match with a search. The earth does not seem to be shared via a split cut out, though I haven't had access to next door to check yet. However, the neighbours supply is apparently on the opposite wall to this one so the earths could well be as good as linked underground.
I realise that RCDs in theory should only monitor the downstream supply, but is there a way that something 'upstream' could cause frequent tripping, or should I forget that and concentrate inside?
On a possibly related note, the resistance of Neutral to Earth external to the supply was about 0.6. Obviously TN-C-S wuold have a low resistance, but TN-S? I am guessing that they tie the outer sheath to earth at the same point as they tie the Neutral to supply for PME?
Any suggestions welcome
Gavin