I have a Gainsborough Energy 2000x Shower which worked perfectly well until the last couple of months. Now after the shower has been on for quite a while the fuse in the main fuse box gets really hot and blows. Does anyone know what the problem might be.
 
Sponsored Links
Do you have the 9.5kW or the 10.8kW model?

How long has the shower been running when the protective device trips?

What type of protective device do you have?

How far away is the shower from that point?

What's the rating (in Amps) of the protective device?
 
Do you have the 9.5kW or the 10.8kW model? 10.8kW

How long has the shower been running when the protective device trips? Approximately 15-20 mins

What type of protective device do you have? 30A Fuse in Main box

How far away is the shower from that point? Approx 8 metres

What's the rating (in Amps) of the protective device? 30A
 
westolly said:
What type of protective device do you have? 30A Fuse in Main box
Even ignoring all other possible factors, this fuse isn't enough for a 10.8kW shower element.

And before you go uprating the fuse, you need to ensure that the cable being
used is adequate, otherwise you may cause a fire.
 
Sponsored Links
Softus said:
And before you go uprating the fuse, you need to ensure that the cable being
used is adequate, otherwise you may cause a fire.

Also as you have a 30A fuse this suggests it is an older type, and the majority of older fuse boxes are not designed to run at over 30A per circuit, and if you do try to use a fuse rated over 30A this may happen, then you really are in trouble.


07112006291.jpg
 
10800 divided by 230 equals FOURTY SEVEN AMPS

NOT THIRTY

This is why your THIRTY AMP fuse is getting HOT and BLOWING.

Who fitted this shower? Why didn't they change the supply arrangements?

You need a FIFTY AMP MCB and RCD feeding that shower. Which probably wont fit in your fuse box, as it was probably never intended for loads over 30 amps per circuit and 60 amps total. If the supply is upgraded to fifty amps, the cable will also need changing to 10mm², its probably 6mm² at the moment.

Get an electrician. ASAP. And DO NOT use that shower again.
 
^maybe it had the wrong (and thus unsafe) fuse wire in before and blew one day when the mains voltage was higher than normal or your shower was longer than normal, and since then its had 30 amp wire in so it keeps blowing -just one possibility.

dont go putting thicker wire in though as even if it was thicker before its notsafe, and even though it didnt go up in flames before its like driving with no seatbelt, just because it didnt kill you before. and as the circuit gets older the chance of it going up in flames increases.

looks like you might need some pro help, but post some photos and we'll point you in the right direction.
 
Crafty said:
10800 divided by 230 equals FOURTY SEVEN AMPS
Note that Gainsborough's rating of 10.8kW is at 240VAC, which yields 45 Amps, not that it would make any difference to the final outcome.
 
westolly said:
But it has been fine for over 4 years so how is it just blowing now?

Is it running for longer?

Here's an overloaded 30A CU...

BurntOutWylexBoard.jpg
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Sponsored Links
Back
Top