How did you wire it up?
PS Did you notify the local authority before starting work
Wasn't aware that you need to notify the local authorities if you are replacing exsisting units with exsisting wiring....
Replacing a CU is notifiable. And how do you know the existing unit was right?Wasn't aware that you need to notify the local authorities if you are replacing exsisting units with exsisting wiring....
The manufacturers, quite correctly, work on the basis that if you don't know how to do it without being told then you shouldn't be doing it.No wiring diagram came with ther unit.
What size cables are you using?So is this the right way to wire this unit?
The Building Regulations draw no such distinction - the concept of "like for like" is not mentioned.Wasn't aware that you need to notify the local authorities if you are replacing exsisting units with exsisting wiring....
If it is a like for like change.
Schedule 2B explicitly makes replacing CUs notifiable.So if your new CU is the same as the old one no need to notify.
No wiring diagram came with ther unit.
The manufacturers, quite correctly, work on the basis that if you don't know how to do it without being told then you shouldn't be doing it.?
4mm armouredWhat size cables are you using?
32ampWhat rating is the breaker in the main CU?
NoIs the main CU circuit RCD protected?
Approx 18mWhat's the distance between the house and the outbuilding?
Without tampering with the Utilites side it seems so.Do you have a TN-C-S supply?
Not sure what you meanAre there extraneous-conductive-parts in the outbuilding?
so extraneous-conductive parts is an alternative earth that the new unit should be hooked up to aswell as the main consumer unit earth??