Right need help with a small question.
Halstead ace high installed, poor hot water, noticed burner pressure was very low (3mb), tried to adjust but not luck. Then tested inlet, found standing to be 24.6 but working fell to 5.1. Completed this test again this time connected to meter test nipple and found very similer results, 24.6 then fell to 6.1.
Meter and govener have both been changed but problem remains, i think it is a blockage etc on external supply pipework but scottish gas guys says its reduced internal pipework.
Any thoughts
Halstead ace high installed, poor hot water, noticed burner pressure was very low (3mb), tried to adjust but not luck. Then tested inlet, found standing to be 24.6 but working fell to 5.1. Completed this test again this time connected to meter test nipple and found very similer results, 24.6 then fell to 6.1.