Looked fairly square and round to me
electrodes out and cleaned
15.06mb on high rate]
Arrived to find EA and flashing lights.
Tried to get the boiler into service mode..
Couldn't get 8F it stopped at 7... returned to 1
Removed siphon bowl and pint of coondense it fired up!
Blew down condense pipe, all clear
Washed siphon trap and tube refitted switched on and no ignition spark..Gas OK
Closed spark gap down to 3-4mm and away it went.
Ran heating and hot water, left heating running.
Waiting for the knock on the door.......................