thanks can cross out all of these though 8 ) RADIATOR PROBLEMS
There are a few causes for the radiators not to get hot.
1) Pump not working or needs bleeding.
pump is fine and atm running on max
2) Insufficient or no water to pump round system. Check boiler pressure if it's a sealed system - should be 1 bar, plus say a third of a bar for every floor more than 3 that there is above the position of the pressure gauge.
For a vented system check the F & E tank has water.
vented system tank has water although needs new cover have now discovered thanks
3) Air lock in heating pipe work (not radiators). Turn off all the other rads to force the flow into the cold one.
Dont think there is air in the pipe work as none of the pipes are rattling and when I took the rad inlet and outlet pipes off water was coming from both even though system was drained (could be my stop cock isnt stop all water.)
4) Air in radiator, which should be removed by bleeding via the bleed screw. This will normally be on one end of the rad, but sometimes they're on the back, covered (or not) with a plastic dome.
Rads all bled fine when recirculating the water.
5) Radiator valve not open or TRV stuck. See post 1
Rad valves all open and heating up on all pipes except the ones on the back room rad.
6) Zone valve or 3 port valve not opening allowing flow to radiators on Y plan or S plan systems. See post 3
no idea about this so could be...
7) System needs balancing which is here
maybe
8 ) Sludge in radiator or pipe work or valve causing blockage which will need to be flushed out.
Was only a small amount of black deposits in the drainage of the rad when drain and the water was dripping from pipes when the rad was taken off.[/b]