Hi,
I have my plumbing first fix in and the plumbers joist holes for the rads start at only 400mm from the joist end. The span is 4400mm which makes the minimum 1100mm by building regs (.25-span).
This plumbing first fix was inspected and past by building control.
Is this common practice for joist holes to be drilled, out of the .25 to .40 span range or is it just down to the inspectors discression? (The plumber did request him to visit before he started work as well)
I will require running my ring main across the plumbing in a couple of places, is there a clearance measurement i need to have when crossing plastic plumbing when clipping it to the joists and would i still require having the joist holes at a minimum of 1100mm?
Thanks,
JC