There in lies the rub..no one really knows how the 470 will work with a manual blending valve for UFH.. the big issue is the relation between a call for heat from the UFH and the compensated temperature that the boiler is working at...
the optimal solution is to use an electronic blender with the VR 68 mixer module...but the valve and motor alone will set you back £250...then there is the pump and the module itself...
The mixer module and the vr 470 allows the system to work with compensated flows..and that means you wont go running around turning things on and off...the way we love to in the UK..it all becomes intervention free..
If it were me I would install a pipe in the bathroom floor as if it were UFH and allow the compensated flow from the boiler to circulate with no controls other than two valve, or if you wanted a TRV... no costly manifolds, NO costly UFH controls and NO separate pump...
As compensated flows settle at about 40-50c, then it doesn't necessarily need to be mixed. But beware if the compensated flow goes up so will the floor temperature...you can over come this with a pipe stat and two port valve. alternatively you could just set the boiler maximum to say 60c
Heat input into floors is limited to avoid damage...
the optimal solution is to use an electronic blender with the VR 68 mixer module...but the valve and motor alone will set you back £250...then there is the pump and the module itself...
The mixer module and the vr 470 allows the system to work with compensated flows..and that means you wont go running around turning things on and off...the way we love to in the UK..it all becomes intervention free..
If it were me I would install a pipe in the bathroom floor as if it were UFH and allow the compensated flow from the boiler to circulate with no controls other than two valve, or if you wanted a TRV... no costly manifolds, NO costly UFH controls and NO separate pump...
As compensated flows settle at about 40-50c, then it doesn't necessarily need to be mixed. But beware if the compensated flow goes up so will the floor temperature...you can over come this with a pipe stat and two port valve. alternatively you could just set the boiler maximum to say 60c
Heat input into floors is limited to avoid damage...