If you could rearrange the circuits to have separate upstairs and downstairs power rings, then have upstairs lighitng and downstairs power on RCD A and downstairs lighting and upstairs power on RCD B.
Ideally I would, I was surprised to find only one ring for all the sockets, I just havent yet worked out the routing of the RF
fair comment! though I know the integrity of this is sound, I installed it myselfPut the shed radial on an RCBO not off one of the RCBs.
Cooker circuit is already there (6mm), its just been extended to the pantry for the fridge/freezer on 2.5mm and will be on a 16APut in a cooker circuit in case you/someone wants leccy cooking at a later date.
I'm not used to doing domestic works, so am just a bit jumpy about having everything on (albeit 2) RCD's, what with 3 fridges and a tumble dryer! I guess these things can be a bit leaky!
I'll split it up to get ballanced loading, see how it works out
Thanks for the advice
Nowt wrong with that, homeboy.
2.5mm on a 16A OPD is fine.