RF Lighting said:All the earth wires in your photo look too small TBH.
There should be a 16.0mm² earth from the supply head to the MET (main earthing terminal) and then a 16.0mm² to each CU.
There should also be a 10.0mm² from the MET to each incomming service to your property (such as gas and water supplies), which I am not sure if they are present.
The current earth supplying your shower CU appers to be 1.5mm² which is woefully undersized. I also notice your shower does not have RCD protection, which whilst it is not a regulation to have, it ceartaint really is a good idea, and vitually all electricians install it as standard.
CU= Consumer Unit, or distribution board, board, or fusebox if you prefer1) whats a CU?
Yes, MET = Main Earthing Terminal, it would be preferable to just have the one, 8 way ones are abaleable2)is the MET the metal earth posts that are clearly visible?
The big black thing that has the suppliers incomming cable going into it and contains the main fuse, it is the property of the supplier3)whats a supply head?
4)i thought the red switchy thing was an rcd for the shower? the black switchy thing on the same isolator looks like an mcb too...je suis tres confused