I see overloaded and stressed MCB's all the time, mostly 6A ones.
I've seen all sorts of brands too. But I too have seen Hager MT106's recently that have broken down.
In the last couple of years,
Actually.......I've had three failed MCB's in as many years, one Geiwess, one Hager and one GET.
Then earlier this year, another Hager MT106 went down.
A strange one it was.
I went to a property to check out an unrelated issue. As I was leaving, I offered to fit a replacement fitting in the hall.
Before I did, I checked the Zs.
It was high, not a fail for a 6A type B, but a lot higher than I'd expect a fitting 6 feet from a DB to be. I checked other fittings on the same circuit: similar high readings. Readings off sockets were normal.
Then the customer said the lighting suffered a great deal of flickering.
I then isolated the MCB. It seemed to switch off a lot easier, with a lot less force than the other MCB's. On a whim, I changed the MCB.
The Zs dropped like a stone, and other readings on the circuit plummeted too. And when I rang the guy later that month, the flickering had stopped too.
So it seemed the MCB was only just holding but causing flickering as the connection was poor and presumably, because of this poor connection, the Zs was being pushed up too.
EDIT in response to RF's post: the Hager MCB's I've replaced have been the older ones with black switches, not the newer type with wider grey ones. Funnily enough, I've not replaced any new ones yet. Installed 100's of them, though... Famous last words.