Would it be better to enter Zs and Zn instead of Zs and PSCC and the calculation to include PEFC as well as PSCC?
I would seem I have moved from original so much. Stage one was from the reading auto taken with a ELI meter to give volt drop and cable length i.e. to verify volt drop with a EICR. ... JohnW2 thought the reverse would be handy working out volt drop and prospective ELI and PSCC at cable destination from cable length and I would agree we see so often "I have a shed/garage at bottom of garden which is 100 meters from house can I use 6mm cable?" ...
As I’ve said, I think that you really need to start by deciding what is the ‘purpose’ of this calculator. If it is intended for
design purposes, then one clearly will not be able to enter any measured values relating the circuit which has not yet been designed/installed (e.g. Zs/PEFC, PSCC or Zn at the end of the circuit). If it is for
design purposes, one needs to be able to enter details about the cable (particularly length), together with Ze (or PEFC at origin of installation) & PSCC (at origin of installation), and thence use the calculator to estimate VD and Zs at the ‘end’ middle for a ring) of the circuit.
If the calculator is intended for some purpose other than design, then it obviously needs to be structured accordingly. If one is talking about an existing circuit, then what obviously matters (for an EICR etc.) are the values of Zs/PEFC (and maybe PSCC)
measured at the ‘end’ of the circuit. About the only thing to be left to be calculated is the VD, and that it a pretty trivial arithmetical exercise once one has the other required measurements.
Also entering prospective short circuit current would also be another option rather than Ze and Zs as it will not involve the earth cables so not going to be messed up with parallel paths ...
Indeed -
if one only wants to calculate VD and PSCC. Again, however, if one wants to use the calculator for design purposes, one won’t be able to enter either Zs or PSCC of the circuit.
Although the
Cleaned up version does the three calculations I am not sure about removing the stages used to arrive at the answer as if I have made an error it's harder to identify.
The old version does allow one to see any striking errors by showing stage information.
I agree totally - it is frustrating not having the intermediate figures there. I think you’re trying move far too quickly. IMO (it’s certainly how I would do it) I think you should leave as many as possible (‘diagnostic’) intermediate results there until you are
totally sure that you have a final and correctly-working version. Then, and only then, should one remove all the ‘unwanted’ outputs.
As you have observed above, one cannot accurately estimate VD from measured Zs/EFLI/PEFC, since those measurements are all affected by ‘parallel paths’. You could do it from L-N loop impedance (or PSCC) if you had measurements both at origin and end of the circuit. The best way, of course, is to calculate VD from an R1+RN (or R1+R2, plus the appropriate adjustment for live/CPC csas - since such ‘dead’ measurements would not be affected by ‘parallel paths’).
Talking of ‘parallel paths’, it’s probably worth remembering that when the calculator is used in ‘design mode’, the calculated estimated Zs will be that which would apply in the absence of parallel paths - if such paths exist, the Zs would obviously be lower, but that wouldn’t matter.
As to temperature and other factors correcting the results it will not alter the answer by much and I do question if it really needs all the inputs. Hence why set to auto enter standard answers. Unless I find some one else's version to compare with hard to really check. Since only to 2 decimal places the results in each version don't exactly match but I feel close enough not to worry about.
I will write separately about the temperature business.
One other issue. For reasons that have been discussed, you use the 26A ‘effective design current’ for calculating VD for a 32A ring final, but I wonder how acceptable this is for ‘official’ purposes (such as an EICR), given that I can find no reference to it in the BGB (which essentially regards the Ib of a 32A ring final as being 32A). This is also of (albeit fairly trivial) relevance in terms of your ‘temperature correction’ calculation, since ‘Equation 6’ calculates ‘Ct’ as a function of Ib/It. I presume/suspect that, for a 32A ring final, your calculator is using the 26A figure for Ib in this equation, and I’m not sure how appropriate/acceptable that is.
On a related issue, as I’ve discussed before, what value of Ib are you intending should be entered for a radial circuit?
Kind Regards, John