Just trying to understand the maths behind table 7.1 in the OSG ... Maximum length
For a 20A RCBO (Type B) cable 2.5 - 1.5 (T&E)
I'm presuming clipped direct as this will give you the longest run
The Maximum Length is 42m.
Now the volt drop calculation. Using Rated current of protective device
18 x 20 x 42 /1000 = 15.12 volts
Which would suggest 42 M is too long
So I must be missing something from my calculation.
And...
Note one says VD is the limiting factor (unless marked ad-ol-zs-sc ) There is no mark.
Max zs is 1.75 for a 20 RCBO/CB, and if Ze was 0.8Ω - would that suggest a max length in relation to Zs as
1.75 - 0.8 = 0.95
0.95 / 0.0195 = 48.7m
No a mile off, but just wondering how the calculations are done.
many thanks