A relative has been having problems with a radial circuit supplying a washing machine and tumble dryer tripping the MCB intermittently.
The Consumer unit was changed about a year ago and a periodic inspection report was supplied, looking at the pir and the CU the circuit is supplied by a 16A mcb. I understand that a radial wired in 2.5mm cable can be run off a 20A mcb, would it be in order to get the MCB uprated to prevent this nuisance tripping? I assume that although the WM is fused at 13A, the MCB is more sensitive and that is why the MCB trips rather than the fuse blowing.
At first the problem only occurred when both appliances were running at once but now they say that it happens when just the WM is operating (the washing machine is also quite new - about 18months or so).
Is the above plan of action OK or does anyone have any other suggestions please?
The Consumer unit was changed about a year ago and a periodic inspection report was supplied, looking at the pir and the CU the circuit is supplied by a 16A mcb. I understand that a radial wired in 2.5mm cable can be run off a 20A mcb, would it be in order to get the MCB uprated to prevent this nuisance tripping? I assume that although the WM is fused at 13A, the MCB is more sensitive and that is why the MCB trips rather than the fuse blowing.