Hi all.
Can someone please tell me the difference between type-B & type-C mcb's?
Can the two types be mixed in the same CU?
Thanks.
 
Sponsored Links
A type B will trip at 3 to 5 times its rated current where a type C will trip at 5 to 10 times rated curent or In. You can use either providing that they will comply with the required disconnection time in the regs. Though on a domestic installation type B is usual, I always use type C on lighting circuits to try an stop the tripping when a lamp blows.
 
Ok, thanks for that. I didn't expect a reply so soon with me posting this late at night. :D
 
Sponsored Links
Yes they can be mixed within same consumer unit - subject to the disconnection times as stated. I always now use Type C's for outdoor power sockets where they are liable to take heavy motor loads with high starting currrents that can trip Type B's.
 