MicroGENUS HE - No hot water/No heat coming through central

Joined
6 May 2004
Messages
104
Reaction score
2
Location
Cambridgeshire
Country
United Kingdom
MicroGENUS HE - No hot water - No heat coming through central heating. (PLEASE HELP!)


1) Boiler make / model (gas or oil)
MicroGENUS HE 24 MFFI (gas)

2) What is / is not happening.
No hot water - No heat coming through central heating system

3) Has ANYTHING else been done or changed recently.
Around a week ago the radiators were checked for excess air in the system. After the air was released from the radiators, the pressure levels shown on the “Central Heating System Pressure Gauge” was below normal causing the boiler to shut down (E 02). Pressure was later reinstated restoring the normal functioning of the boiler.

4) When did the problem start?
Just over 24 hours ago. When the boiler appeared inactive (no hot water), displaying the error code E 34.

5) When does it happen? eg, heating coming on or going off.
As soon as we realized the water wasn’t heating up, we checked the radiators and they were still warm, indicating the boiler stopped its normal function presumably very shortly previous to the lack of heat in the tap water.

6) Anything else you feel may be of relevance.
After attempting to re-start the boiler we encountered an error code we never seen before: A 03 indicating the boiler reached or exceeded the 103°, causing it to shut down of course. We followed the instructions and allowed the boiler to cool down before attempting to re-star it, only to see the same problem reoccurring. We did this several times to no avail.
This morning the boiler displayed a rather encouraging “on” reading on the digital display, with the central heating off and the “hot water temperature adjustment” on 3, we turn the tap on. Again no hot water. The boiler fired up making strange noises, steam was coming through the external exhaust (flue), but the digital display was showing a fixed temperature of 11, only to fluctuate briefly towards 14 and later plummeted below 10.
Next we tried to turn the central heating on.
Same as with the hot water, noises and steam. But now the digital display was going crazy from a temperature of around 34/40° raising to over 65 in less than 5 seconds and still raising. This gave us the indication that it was about to over heat again so we immediately switched the central heating dial OFF and desisted any further attempts on the boiler.


- Any assistance/advice will be highly appreciated - [/u]
 
Sponsored Links
Ah well if you don't ask you don't learn.......

From the manual:
Other Shutdown Situations
Should a shutdown situation indicated on the display by the following letters and figures occur, E04, E05, E06, E07, E08, E09, E20, E21, E33, E34 contact one of our Authorised Service Centres.
:rolleyes: :rolleyes: :rolleyes: :rolleyes:

Overheating is likely to be due to air stuck in the boiler - make sure the auto air vent cap is loose,
or the pump not running - make sure it isn't stuck. (see faq)
 
Many thanks for your prompt reply ChrisR.

If I would have it my way… I’d rip the boiler and the entire central heating radiators system a set fire to them doing a little dance around the bonfire. I’d replace them by a individual gas heaters and a straight forward - box standard boiler for hot water.
Unfortunately, as right now I must deal with this monstrosity of a creation that is this unnecessarily complicated, unstable and unreliable boiler/central heating combi that was no doubt intentionally designed to be a complete fiasco from its conception.

But back on topic…!

Consulting the “installation and servicing instructions” manual (using the term “manual very loosely here) I noticed the “auto air vent cap” and indeed the “pump” are located just behind the “time clock/pressure gauge” panel, shown on page 54 (6.5.4/6.5.5).
And also again it can be viewed on page 7 of the “brochure microGENUS”
http://www.heatweb.com/pdf/Ariston/brochure_microGENUS.pdf

Q; Is this correct?

Assuming that we manage open the panel and access the pump and air vent cap, what should we do/check next? Or what would give us the indication (as you advised) that the “auto air vent cap is loose” and/or the “pump isn’t stuck“?

And finally would the opening of the panel invalid the guaranty? The boiler was installed about a year ago.

-Again thanks-
 
Sponsored Links
well here we go E34 is a faulty air pressure switch unfortunately even the new ones they supply dont work very well.AO3 is either a stuck pump there is a fault with them,but they also stick if the system has not been flushed properly,or the overheat stat on the pipe on the left of the heat exchanger is faulty check that the connection on it is still in place as they tend to drop of if fitted to close to the heat exchanger body, A79 is a faulty recouperator they also have faults,A01 is a faulty main pcb they have faults to,best advise is sorry take out an insurance policy,good luck
 