Hopefully not.D. Will they want to see locking off devices used on mcb's and signs?
Signs are of no value to anyone, they can easily be removed, not read, not understood.
MCB locking devices in a domestic environment are generally cack as well - a good many can easily be removed without tools or the key. Then there are those countless installations where it is impossible to fit such things.
The proper method for isolating the circuit is to remove the line and neutral conductors from the MCB / neutral bar / RCBO or other device and put them in the earth bar.
This ensures no one can switch the circuit on, avoids the whole-house RCD tripping when you mistakenly connect N&E together when removing a socket, and it means you can confirm the circuit you disconnected is the correct one (test for continuity between the three conductors), and it also eliminates any possibility of that circuit becoming energised from some other source such as when two or more circuits are connected together due to fools and blunderers having worked on it previously.