Hi (great forum by the way), my boiler had a problem where the hot water was calling constantly but i managed to fix it by changing the microswitch. It has now developed a further problem where it fires up but after about 20 mins the flame goes out, I can still hear the fan and the thermostat is on full for both water and heating (I have tried it on lower too) I have also tried the same on just water setting too. I thought it might be the temp sensor so I took a cold reading and it was 11K ohms which is fine then I ran the boiler until it cut out and the reading was 4K ohms (is that about normal?).
I have to wait quite a while before it will fire up again (30 mins+)
One thing that is strange is that when it cuts out or if I turn the thermostat down it wont fire up if I turn it back up but the fan still goes.
Any suggestions or further tests would be much appreciated. Thanks
I have to wait quite a while before it will fire up again (30 mins+)
One thing that is strange is that when it cuts out or if I turn the thermostat down it wont fire up if I turn it back up but the fan still goes.
Any suggestions or further tests would be much appreciated. Thanks