Hi
My performa 24 combi refuses to fire up when CH/DHW is demanded. I have been through the fault finding in the manual but it hasn't helped-
DHW for example:
pressure switch operates diaphragm OK
microswitch provides 230V
pump runs
fan runs
air pressure switch provides 230V
ignitor does NOT receive 230V.
However, I have replaced PCB (according to manual) with same result.
Over-temp thermistor hasn't tripped, correct resistance from temp sensor, correct DC volts to gas valve.
Any ideas?
If I provide 230V to the ignitor the system works OK, but requires ignitor to be on constantly to sustain the burner - is this correct behaviour? has the flame-sensing electrode gone, what voltage should I see on it when burner is lit?
Really appreciate any suggestions.
Cheers.